I got this email from one of our Electrical Engineers. Below is what he is wanting but I haven't figured out a way to build it for him. The problem I think is that with a panelboard family it doesn't give you a secondary distribution system. But a transformer family does give you the secondary, but then it doesn't have a panel schedule. Have any of yall found a way around this. If you need more info let me know, Thanks!
_______________________________________________________________________
I need the Operating Room Isolation Power Panels to have the following properties:
1. 480V, 1-Phase, 2-Pole Input Voltage.
2. 208V, 1-Phase, 2-Pole Output Voltage.
3. Transformer Information: 480V, 1-Phase to 208V, 1-Phase.
4. The panel schedule shall have all 120V 2-Pole loads.
These are power isolation panels installed in Operating and C-Section Rooms which measure the stray grounding current and isolate the O.R./C-section room grounding system from the rest of the building’s grounding electrode system. The isolation panels are manufactured by Square D and are found in the Medical Products section of the Square D digest. Since it is basically a transformer and panel combined, it may need to be built as two separate families (transformer and panel).