Thread: gbxml and load calc errors

  1. #1
    Member
    Join Date
    2009-03
    Posts
    5

    Default gbxml and load calc errors

    If you draw walls in the wrong order you can end up in a situation where Revit interrupts south facing glass in a north facing wall. I'm sure you're all aware that glass orientation has a considerable impact on the building loads.

    Steps to reproduce:
    1. Open a new file in Revit MEP 2011 x64 w/ web update 2 service pack
    2. Draw a rectangle room with 4 generic 8” walls 20’ tall.
    3. Draw 10’ tall curtain wall into the north wall FROM LEFT TO RIGHT, in other words start in the northwest corner of the building and draw to the northeast corner.
    4. Cut the curtain wall out of the generic 8” wall.
    5. Place a space in the room and change the upper limit offset to 12’.
    6. Open gbxml export and change export complexity to Complex and click Save Settings.
    7. Open Heating and Cooling Loads and click Analytical Surfaces. Notice the generic 8” wall to the north is considered a north wall, however the curtain wall cut out of the generic 8” wall to the north is considered south facing glass.
    8. Change the Report Type to Detailed and click calculate. Scroll down to the space summary and notice there is a huge south window load although there is no south facing glass. Notice there is no north window load although there is north facing glass.

    I contacted my reseller and Autodesk a couple times and neither responded, so just beware that using Revit's load calculator is still in need of refinement.
    Attached Images Attached Images

  2. #2
    Member
    Join Date
    2006-11
    Posts
    42

    Default Re: gbxml and load calc errors

    Thanks for the feedback. I will report this problem.

  3. #3
    I could stop if I wanted to gabecottam's Avatar
    Join Date
    2006-10
    Posts
    236

    Default Re: gbxml and load calc errors

    Question Anna:
    Who are you reporting to?
    The OP and I have tried to report this issue to William Spier both directly and through our local reseller on multiple occasions, but he seems to have selective hearing. I'm hoping you have access to a more responsive ear at "the factory".

    We would love some sort of acknowledgment that they are aware this problem exists - and have, at least, added it to their long list of things that need fixing.
    Gabe Cottam . . . . Sr. AEC Application Engineer . . . . ProSoft

  4. #4
    Member
    Join Date
    2006-11
    Posts
    42

    Default Re: gbxml and load calc errors

    Sorry for making a vague statement on where I reported the problem. The problem has been filed and sent to the development team for investigation.

    Sincerely,
    Anna Oscarson
    QA Analyst
    Autodesk, Inc.

Similar Threads

  1. 2011: Autodesk's HVAC Load Calc Extension standalone program
    By wboyanton in forum AMEP General
    Replies: 3
    Last Post: 2010-11-16, 11:42 AM
  2. Fatal Errors, run time errors
    By carmen.martinez in forum AutoCAD General
    Replies: 2
    Last Post: 2008-04-17, 02:12 PM
  3. G.S.F. Per Bed Calc
    By krista.manna in forum Revit Architecture - General
    Replies: 8
    Last Post: 2006-11-06, 07:50 PM
  4. Occupancy Load Form - Spread Sheet calc.
    By rhayes.99001 in forum AutoCAD Customization
    Replies: 4
    Last Post: 2005-12-22, 09:25 PM
  5. Occupancy Load Calc
    By pwmsmith in forum Revit Architecture - Families
    Replies: 1
    Last Post: 2005-12-04, 02:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •