Thread: Victaulic Fire Protection Piping

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Member
    Join Date
    2013-02
    Posts
    4
    Login to Give a bone
    0

    Default Victaulic Fire Protection Piping

    We tried autorouting piping with the family Fire Protection Piping from Victaulic, and it can only make 45º and 90º turns (elbows).

    We can not route the pipes in the exact way we have it in the design, because we have many angles in the turning points.

    Anyone faced this problem? Victaulic has not answered so far.

    thanks

  2. #2
    Certifiable AUGI Addict Dimitri Harvalias's Avatar
    Join Date
    2015-12
    Location
    Vancouver, BC Canada
    Posts
    3,753
    Login to Give a bone
    0

    Default Re: Victaulic Fire Protection Piping

    Welcome the forums.
    I'm not familiar with the details of the Victaulic families but does Victaulic make fittings for 'custom' angles outside of what they supply in their families? As far as I know you're limited to 90, 45, 22.5 and 11.25 degrees in the 'real' world right?

  3. #3
    Member
    Join Date
    2013-02
    Posts
    4
    Login to Give a bone
    0

    Default Re: Victaulic Fire Protection Piping

    Thanks for your reply. I checked Victaulic webpage and it looks like they have real pipe elbows with 11.25 and 22.5 degrees, but the revit family that is available for download only has 45º and 90º, which limits the routing posibilities.

  4. #4
    AUGI Addict
    Join Date
    2002-06
    Location
    North Central CT
    Posts
    1,108
    Login to Give a bone
    0

    Default Re: Victaulic Fire Protection Piping

    Just wanted to add my 2 Pesos worth... Auto-routing is a useless feature and I say this because in the real-world, you will have various obstructions to work around such as other pipes, ducts, cable trays, steel, etc...

    It's a nice idea but the practicality of it.... well, it isn't practical at all unless you're modeling an open ceiling space like a large warehouse. In that case you MIGHT be able to use it.

    Matt

  5. #5
    Member
    Join Date
    2013-02
    Posts
    4
    Login to Give a bone
    0

    Default Re: Victaulic Fire Protection Piping

    I put it wrong. In fact we are placing pipes with the "pipe" command in the systems ribbon, not using autorouting.

  6. #6
    I could stop if I wanted to
    Join Date
    2011-01
    Posts
    226
    Login to Give a bone
    0

    Default Re: Victaulic Fire Protection Piping

    So the problem is that the fittings won't use any angle except 45 and 90, right? If that's the case, perhaps the family is created in such a away as to only allow those angles. Take a look inside an elbow family and check what parameter is controlling the bend angle. Then check whether that parameter is constrained to certain angles.

  7. #7
    Member
    Join Date
    2013-02
    Posts
    2
    Login to Give a bone
    0

    Default Re: Victaulic Fire Protection Piping

    The family you are using only contains the 90 degree (No. 001) and 45 degree (No. 003) elbows. These are the only angles available in the FireLock Fire Protection product line per our product submittal 10.03. We do offer 90 degree (No. 10), 45 degree (No. 11), 22.5 degree(No. 12) and 11.25 degree (No. 13) elbows in our IPS Revit family. These are the only standard angle elbows we offer. If you require additional information on the IPS product line please download submittal 07.01 from the Victaulic website.

  8. #8
    Member
    Join Date
    2013-02
    Posts
    2
    Login to Give a bone
    0

    Default Re: Victaulic Fire Protection Piping

    We could also recommend using flexible couplings to arrive at small needs for deflection.

  9. #9
    I could stop if I wanted to
    Join Date
    2011-01
    Posts
    226
    Login to Give a bone
    0

    Default Re: Victaulic Fire Protection Piping

    Often in the field two 45 degree bends will be used together in order to achieve non-standard angles. So essentially there becomes no angle restrictions. Unfortunately, doing that in a Revit model would create all sorts of headaches - fitting to fitting connections, way too many elevation values for pipe runs, etc. Rather, "unlocking" the fitting from those standard angles, then using the "IsCustom" parameter built into fitting families to alert the user to those non-standard angles allows for more flexibility.

    Just my 2 cents.

  10. #10
    Member
    Join Date
    2013-02
    Posts
    4
    Login to Give a bone
    0

    Default Re: Victaulic Fire Protection Piping

    I received an answer from Victaulic. The tables appear to be misplaced in the computer.

    Thanks all for the repplies

Page 1 of 2 12 LastLast

Similar Threads

  1. 2013: Fire Protection
    By Mike L Sealander in forum Revit Architecture - General
    Replies: 1
    Last Post: 2013-04-23, 01:34 AM
  2. Fire Protection piping and sprinkler head layout
    By rrubert in forum Revit MEP - General
    Replies: 0
    Last Post: 2010-07-28, 08:55 PM
  3. Fire Protection
    By buzz in forum AMEP General
    Replies: 0
    Last Post: 2007-11-15, 11:18 PM
  4. Fire Protection Symbols
    By dazza163968596 in forum Revit Architecture - Families
    Replies: 1
    Last Post: 2004-11-21, 11:00 AM
  5. Fire Protection piping
    By crarchitect in forum Revit Architecture - General
    Replies: 4
    Last Post: 2004-09-17, 03:15 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •