    Default Split Bus Electrical Panel

    Trying to create a split bus panel with Integrated Transfer Switch that I can circuit 100% of the load to a Main Distribution Panel and also only circuit the Emergency Circuits on that Split Bus Panel to an Emergency Generator Distribution Panel. Chances are it will require a second connector on the split-bus panel, I just don't want to fill in the emergency load manually on the connector (or by radio), I would like Revit to do this calculation for me and ideally be able to choose what circuits are emergency and only tally those loads when circuited to the GDP.

    This is the actual split bus panel:
    RPFL-NEMA1-0609_low%20res - Bluebeam Revu x64_2014-04-17_10-47-05.png

    This is the Diagram of how I would like to Circuit it in Revit:

    Split Bus Diagram.png

    Thanks

  2. #2
    I could stop if I wanted to
    Join Date
    2010-01
    Posts
    364
    Login to Give a bone
    0

    Default Re: Split Bus Electrical Panel

    You'll probably have to use two separate panelboard instances for each portion of your split bus panel.

  3. #3
    Active Member
    Join Date
    2011-09
    Location
    Miami, Fl
    Posts
    57
    Login to Give a bone
    0

    Default Re: Split Bus Electrical Panel

    If I did that, I would have to add a second connector to all the Electrical Fixtures that are also Emergency, to be able to circuit them to both panels.

  4. #4
    I could stop if I wanted to
    Join Date
    2015-11
    Location
    Saint Louis, MO
    Posts
    485
    Login to Give a bone
    0

    Default Re: Split Bus Electrical Panel

    I would use 2 separate panels, maybe stacked on a wall so they'll show as one in plan. if your emergency panel is sub-fed from a breaker in the normal panel, then you'll be able to get total emergency load and total combined loads, they will go thru to the bus of the normal panel via the 3-pole breaker. you will have 2 separate panel schedules, but your math would be correct. I think you'll have to fake and size yourself the emergency feeder to the generator for your plans/one-line. revit won't care at that point.
    hth,
    mike

  5. #5
    Active Member
    Join Date
    2011-09
    Location
    Miami, Fl
    Posts
    57
    Login to Give a bone
    0

    Default Re: Split Bus Electrical Panel

    Quote Originally Posted by mhartmann View Post
    I would use 2 separate panels, maybe stacked on a wall so they'll show as one in plan. if your emergency panel is sub-fed from a breaker in the normal panel, then you'll be able to get total emergency load and total combined loads, they will go thru to the bus of the normal panel via the 3-pole breaker. you will have 2 separate panel schedules, but your math would be correct. I think you'll have to fake and size yourself the emergency feeder to the generator for your plans/one-line. revit won't care at that point.
    hth,
    mike
    But this would be a manual load that I would have to calculate from the Main Panel's Emergency Circuits to input into the Emergency Panel to then circuit to the GDP. I would like Revit to do this for me instead.

Similar Threads

  1. 2014: Electrical Panel Schedule (1-Phase Panel to a 3-Phase Panel)
    By Binu Mathew in forum Revit MEP - General
    Replies: 3
    Last Post: 2015-03-26, 02:56 PM
  2. 2014: Electrical panel schedules for split load board
    By ncharlwood389454 in forum Revit MEP - General
    Replies: 6
    Last Post: 2015-02-16, 02:23 PM
  3. Electrical Panel
    By johnny138421 in forum AMEP General
    Replies: 3
    Last Post: 2011-03-25, 09:54 AM
  4. Split up Number of Elements in Panel Schedule
    By drewj in forum Revit MEP - General
    Replies: 2
    Last Post: 2011-02-24, 08:55 PM
  5. Electrical - Panel GPO
    By donovans in forum Dynamic Blocks - Sharing
    Replies: 2
    Last Post: 2007-02-16, 03:36 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •