I have two questions on schedules.

1: Is it possible to have a schedule wide variable that is used in formulas? I imagine a schedule of floor areas, with a field in which you type in a "Usable ratio", say .85, and all the areas are multiplied by 85%. Change the Usable ratio field to .9 and all the areas update. And I would prefer the value not to be a project parameter or anything, because I might use different values in different schedules. I want it to be an input value on the specific schedule, and the schedule plays spreadsheet and multiplies by A1.

2: Is it possible to limit a schedule to contents within a scope box? As in the above areas schedule, where you have two towers, two scope boxes, and two schedules that each schedule just one tower?

Thanks all,
Gordon

aggockel50321
2006-11-07, 02:24 PM
1. You can create a shared project parameter tied to floors, & use it in a calculated value formula in your schedule. The value will can be unique (and changeable) for each floor in the project.

I don't think you can do it by scope box, but you can filter the schedule by any parameter that's used as a field, including shared project parameters that you create just for filtering.

ijnicholas
2006-11-07, 04:25 PM
1. In the Schedule Properties, there is a "Calculated Value..." tool button. You could use this to create a new column "Usable ratio". (For the type, select "Area" and in the Formula field enter "Area * 0.85". This achieves your requirements without adding any parameter. To create another Schedule with a different ratio, you have to just duplicate the schedule and change the formula ("Area * 0.7")

2. Not with a scope box, but there are so many workarounds. You could name your areas with a prefix "1-" for the tower 1 areas and you could sort based on the "name" and "begins with" option.

nicholas.

travismv702230
2006-11-09, 04:06 PM
I have a similar question regarding formulas in schedules...

I have a room schedule for my Life Safety Plan. I have already created parameters for the types of occupancy (storage, unconcentrated assembly, office, etc.).

Now, I want to create a formula that takes the square footage of the room and divides it by the appropriate number so I can figure out the occupant load. For example, assign 1 person per 100 sqft for office, 1 to 15 for unconcentrated assembly, 1 to 300 for storage, etc.

Anyone have any experience in this? Ideas?

Thanks,
Travis

aggockel50321
2006-11-09, 06:18 PM
One method:

You could set up a project parameter tied to rooms, called say Ft per Occ, whose type is area.

Then within the room schedule, set up a calculated value as an integer, whose formula would be:

Area/Ft per Occ - .5

Subtracting .5 from the result will truncate the result, rather than rounding it to form the integer.