Thread: Voltage Drop - How does your firm do it?

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    100 Club
    Join Date
    2007-08
    Location
    Rogers, AR
    Posts
    103
    Login to Give a bone
    0

    Default Voltage Drop - How does your firm do it?

    I am interested in hearing how other electrical engineers and firms do their voltage dropping, mainly for circuits with multiple fixtures (ie, lighting runs). The reason I ask is because the way we do it seems to be completely different than the way Revit does it...

    The way we have done it for years is to use the "electrical center" of a circuit, and then run parallel and/or perpendicular to walls all the way back to the panelboard. So, for instance, if you have a run of lights that are the same, and equally spaced, then the "electrical center" of the circuit will be in the middle of the run. If you have a circuit with different loads spaced sporatically around the area, then it is obviously harder to find the exact center. On a project I am currently working on, I had determined that the electrical center of the circuit was ~75' from the panelboard.

    Now, from what I can gather (since I don't think its actually spelled out anywhere), Revit uses the entire length of the circuit for voltage drop. I built a schedule to return values similar to our in-house voltage drop spreadsheet, and found that Revit returned a value of 175'.

    This now caused the circuit to go from #12 wire to #8 wire. When I plugged the same values into our in-house spreadsheet, I found that with #10 wire, the resulting voltage drop was 3.02% (I had it specified in Revit for 3%). So for us, we feel the built in wire sizing in Revit is invalid and not usable, which sucks. So my question is, is anyone else under the same opinion? Or have you even checked it against the way you were doing it before Revit?

  2. #2
    All AUGI, all the time JoelLondenberg's Avatar
    Join Date
    2015-10
    Posts
    508
    Login to Give a bone
    0

    Default Re: Voltage Drop - How does your firm do it?

    I don't know of any firm using Revit's voltage drop/wire sizing.

  3. #3
    100 Club
    Join Date
    2007-08
    Location
    Rogers, AR
    Posts
    103
    Login to Give a bone
    0

    Default Re: Voltage Drop - How does your firm do it?

    Maybe that should be a note for Autodesk then...

  4. #4
    Revit Forum Manager Steve_Stafford's Avatar
    Join Date
    2001-12
    Location
    Irvine, CA
    Posts
    7,567
    Login to Give a bone
    0

    Default Re: Voltage Drop - How does your firm do it?

    Scott with RLBA shared a nice pdf of his effort to determine how various length of various circuits are defined. It boils down to an X/Y relationship to the furthest parts of the circuit, adding the X distance and Y distance to arrive at an "arbitrary" estimate for length. I'm not sure how they can ever be "accurate". You'd have to run actual wiring to even get close, up and over doors/openings, into plenum and down under floors...over the wood and through the snow.

    I suppose it would be better to be able to define some "length calculation" criteria like take the total distance and "divide by 2". Take your scenario and codify it??

  5. #5
    100 Club
    Join Date
    2007-08
    Location
    Rogers, AR
    Posts
    103
    Login to Give a bone
    0

    Default Re: Voltage Drop - How does your firm do it?

    That is an interesting evaluation. I attempted that method with my circuits, and I still can't seem to get anywhere close to what Revit is returning. If it factors in switching, it might be slightly closer, but I still don't see it even within 20%... I have included the lighting and circuitry I am currently working on (small tenant space). The panelboard is not shown, but it is right below the 3-way switch on the far right of the page. For circuit 1, Revit returned 138'. For circuit 3, Revit returned 174'. I have no measurements shown, but you can get a general idea of size based on the 2x4 troffers shown on circuit 1.
    Attached Files Attached Files

  6. #6
    Revit MEP Moderator mjdanowski's Avatar
    Join Date
    2007-03
    Posts
    890
    Login to Give a bone
    0

    Default Re: Voltage Drop - How does your firm do it?

    In Excel/SKM

    The fact that Revit just spits out a number without any explanation or display of factors which it used to get there is simply not something we can use.
    Matthew Danowski, PE, LEED AP BD+C
    Project Electrical Engineer
    Baltimore, MD

Similar Threads

  1. 2014: drop voltage and cable setting
    By MEP2 in forum Revit MEP - General
    Replies: 3
    Last Post: 2015-05-26, 12:19 PM
  2. 2014: drop voltage
    By MEP2 in forum Revit MEP - General
    Replies: 0
    Last Post: 2015-05-26, 11:54 AM
  3. Voltage Drop
    By Brian Myers in forum ACA/AMEP Tips & Tricks
    Replies: 4
    Last Post: 2011-04-04, 12:25 PM
  4. [2010] Voltage Drop Percentages (OPEN)
    By heiko.stugg in forum Revit MEP - Wish List
    Replies: 1
    Last Post: 2010-03-15, 05:38 PM
  5. Calculate voltage drop in Revit MEP
    By baji-gal.ferenc in forum Revit MEP - General
    Replies: 7
    Last Post: 2009-11-04, 04:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •