Thread: Replacing windows with with new windows of the same size

  1. #1
    Member
    Join Date
    2009-12
    Location
    North of Seattle
    Posts
    24
    Login to Give a bone
    0

    Default Replacing windows with with new windows of the same size

    Ok, we've ran into a bit of a workflow (I think) issue with Revit 2010.

    We've got a renovation project. Some existing windows are being replaced with new windows and the new ones are the same size as the previous.

    So, as I remember it (as I'm typing this from home).

    1. There's a 5'x8' window in an existing wall.
    2. The window is demolished in the demo phase.
    2a. Revit then creates a wall infill in place of the removed window.
    3. We try to install a 5'x8' window but can't as the infill is the same size as the infill. The infill is a separate wall segment and with the window being the same size there is then no wall left for hosting the window.

    The work around we've done is to install the window as close as possible and have it nudged over just a bit so it's replacing 99.5% (or so) of the infill and a sliver of the original wall.

    Is this a problem with Revit that others are seeing or are we just looking at this issue incorrectly?

    Thanks.

  2. #2
    AUGI Addict cdatechguy's Avatar
    Join Date
    2006-10
    Location
    CdA, ID
    Posts
    1,533
    Login to Give a bone
    0

    Default Re: Replacing windows with with new windows of the same size

    Yeah, the infill thing is pretty messed up....(think this was a wishlist item)

    What I do is cutout the wall where the window will be demo'd...then I demo the wall, not the window...thus no infill....then you can put in a new wall and window or put a non-hosting window in its place...
    Michael "MP" Patrick
    "I only drink :coffee: until it's acceptable to drink :beer: or :whiskey: or :wine:"

  3. #3
    Certified AUGI Addict patricks's Avatar
    Join Date
    2004-06
    Location
    Memphis TN area
    Posts
    7,048
    Login to Give a bone
    0

    Default Re: Replacing windows with with new windows of the same size

    I have also run into this, and I have been able to get it to work by placing the new window so that it cuts both the existing wall and the infill wall, and then moving it over into the correct location. Sometimes I also have to do various join operations between the existing and infill walls, but I can usually get it to work.

Similar Threads

  1. Renovation - replacing LOTS of doors and portions of windows
    By patricks in forum Revit Architecture - General
    Replies: 9
    Last Post: 2010-06-30, 09:35 PM
  2. Retaining Size, Location of Dockable Windows
    By rbdome in forum AutoCAD CUI Menus
    Replies: 4
    Last Post: 2007-09-10, 11:58 PM
  3. Window Tags w/ size of windows
    By Matt Mercer in forum Revit Architecture - Families
    Replies: 20
    Last Post: 2005-09-30, 10:42 PM
  4. adjusting size of windows
    By k.armstrong in forum Revit Architecture - General
    Replies: 2
    Last Post: 2004-11-28, 04:33 PM
  5. Variable Size Windows?
    By Archimac in forum Revit Architecture - General
    Replies: 9
    Last Post: 2004-07-28, 01:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •