Thread: 2011 Multiple Electrical Connectors

  1. #1
    Woo! Hoo! my 1st post
    Join Date
    2011-08
    Posts
    1
    Login to Give a bone
    0

    Default 2011 Multiple Electrical Connectors

    I have created a family with (2) electrical connectors, for which I am setting different demand factors.

    I would like both connectors to be circuited to the same circuit. However, when I circuit one connector, I cannot add the other connector to the same circuit.

    Any ideas?

    Thanks.

  2. #2
    100 Club
    Join Date
    2010-03
    Location
    Nashville, TN
    Posts
    106
    Login to Give a bone
    0

    Default Re: 2011 Multiple Electrical Connectors

    You might try placing another Device and adding it to the circuit. Then select that new device, edit circuit and add the remaining connector from the first device. Once all three are connected you can remove the extra device.

  3. #3
    Revit MEP Moderator mjdanowski's Avatar
    Join Date
    2007-03
    Posts
    890
    Login to Give a bone
    0

    Default Re: 2011 Multiple Electrical Connectors

    What piece of equipment requires two demand factors and needs to be on the same circuit?
    Matthew Danowski, PE, LEED AP BD+C
    Project Electrical Engineer
    Baltimore, MD

  4. #4
    100 Club
    Join Date
    2010-03
    Location
    Nashville, TN
    Posts
    106
    Login to Give a bone
    0

    Default Re: 2011 Multiple Electrical Connectors

    I was wondering the same thing. Maybe an AHU but typically that would be two circuits. Fan - motor, compressor - hvac.

  5. #5
    Member
    Join Date
    2011-05
    Posts
    12
    Login to Give a bone
    0

    Default Re: 2011 Multiple Electrical Connectors

    you could need two demand factors if an AHU has a large electric heat section in it. That electric heat, depending on the climate where the project is could have a lower demand than normal. Its an odd situation, but does come up.

    You definitely needd two connectors if the above is true. I had one AHU once that had a ~25hp supply fan and 400A of heat, I needed a seperate circuit for the darn heat.

  6. #6
    Revit MEP Moderator mjdanowski's Avatar
    Join Date
    2007-03
    Posts
    890
    Login to Give a bone
    0

    Default Re: 2011 Multiple Electrical Connectors

    Quote Originally Posted by Monza View Post
    you could need two demand factors if an AHU has a large electric heat section in it. That electric heat, depending on the climate where the project is could have a lower demand than normal. Its an odd situation, but does come up.

    You definitely needd two connectors if the above is true. I had one AHU once that had a ~25hp supply fan and 400A of heat, I needed a seperate circuit for the darn heat.
    A large electric heat will have a separate connection (or at least will be able to connected separately)

    Only small heat elements will be tied into the fan (which is usually small as well)
    Matthew Danowski, PE, LEED AP BD+C
    Project Electrical Engineer
    Baltimore, MD

  7. #7
    100 Club
    Join Date
    2007-08
    Location
    Rogers, AR
    Posts
    103
    Login to Give a bone
    0

    Default Re: 2011 Multiple Electrical Connectors

    A self-contained refrigerated case could have a single feed with multiple demand factors for lighting, fans (continuous), and defrost (non-continuous).

Similar Threads

  1. 2014: Electrical Connectors Wrong Position
    By thom.chase676847 in forum Revit MEP - General
    Replies: 3
    Last Post: 2014-07-30, 02:14 PM
  2. 2011: Renumber electrical connectors
    By matt__w in forum Revit MEP - General
    Replies: 0
    Last Post: 2013-01-18, 07:23 PM
  3. Multiple Electrical Connectors
    By repp in forum Revit MEP - Families
    Replies: 4
    Last Post: 2012-11-09, 03:20 PM
  4. Visibility of electrical connectors
    By Wish List System in forum Revit MEP - Wish List
    Replies: 1
    Last Post: 2012-10-05, 04:33 PM
  5. Electrical Connectors
    By trent.chambers in forum Parts Builder
    Replies: 1
    Last Post: 2010-06-09, 07:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •