Thread: Mechanical equipment family with nested families cannot be selected as equipment for the duct system

  1. #1
    I could stop if I wanted to
    Join Date
    2008-02
    Location
    Austin, TX
    Posts
    210
    Login to Give a bone
    0

    Default Mechanical equipment family with nested families cannot be selected as equipment for the duct system

    I downloaded a Johnson Controls Rooftop unit (attached), and everything looks great until I try to select it as the Equipment for my duct system. I can select an out of the box VAV, but not the Johnson Controls RTU. The family uses nested families that are categorized as Mechanical Equipment, so I changed those to Generic Models, but I still can't select the unit as my equipment for the duct system. Any idea what's going on?

  2. #2
    All AUGI, all the time CADastrophe's Avatar
    Join Date
    2012-01
    Location
    Site of the next CADaclysm
    Posts
    813
    Login to Give a bone
    0

    Default Re: Mechanical equipment family with nested families cannot be selected as equipment for the duct system

    Are the Connectors part of the nested families? Revit cannot connect to them if they are buried within a nested family.

  3. #3
    I could stop if I wanted to
    Join Date
    2008-02
    Location
    Austin, TX
    Posts
    210
    Login to Give a bone
    0

    Default Re: Mechanical equipment family with nested families cannot be selected as equipment for the duct system

    Quote Originally Posted by CADastrophe View Post
    Are the Connectors part of the nested families? Revit cannot connect to them if they are buried within a nested family.
    No the connectors are part of the parent family. I can actually connect to it just fine with ductwork, I just can't select it as the equipment for that system, so in my System Browser, only the air terminals show up for that system.

  4. #4
    All AUGI, all the time CADastrophe's Avatar
    Join Date
    2012-01
    Location
    Site of the next CADaclysm
    Posts
    813
    Login to Give a bone
    0

    Default Re: Mechanical equipment family with nested families cannot be selected as equipment for the duct system

    It's becuase the Supply Air Connector's Flow Direction is set to "In". Change it to "Out" and you can select it.

  5. #5
    I could stop if I wanted to
    Join Date
    2008-02
    Location
    Austin, TX
    Posts
    210
    Login to Give a bone
    0

    Default Re: Mechanical equipment family with nested families cannot be selected as equipment for the duct system

    Quote Originally Posted by CADastrophe View Post
    It's becuase the Supply Air Connector's Flow Direction is set to "In". Change it to "Out" and you can select it.
    Bingo. Didn't even think to look at that, thanks!

Similar Threads

  1. Circuiting Mechanical Equipment grabs non-selected elements
    By Armando Martinez in forum Revit MEP - General
    Replies: 5
    Last Post: 2016-01-20, 11:20 PM
  2. Replies: 4
    Last Post: 2012-02-15, 08:54 PM
  3. Replies: 0
    Last Post: 2011-12-09, 04:32 PM
  4. Revit duct connectors mechanical equipment
    By tim99 in forum Revit MEP - General
    Replies: 3
    Last Post: 2011-02-05, 12:57 AM
  5. Custom mechanical equipment family
    By awascher in forum Revit MEP - Families
    Replies: 3
    Last Post: 2008-09-03, 04:40 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •