I have uploaded screenshots from a test model.
My ultimate question is this: shouldn't the amps per phase for the circuit feeding the panel be the same as the amps per phase on the panel (and reported on the panel schedule)? Refer to the screenshots. Shouldn't the amps per phase on MS 208 - 1 be the same as the amps per phase on Panel 208 panel schedule?
BTW, this discrepancy occurs using all OOTB settings. families, etc. as well. So I feel reasonably confident it isn't something in our template or families.
I have a panel with a 3 phase load and a single phase 2 pole load. Refer to Panel_208. The load for the entire panel is correct, as is the current for the entire panel. However, how it is calculating total amps per phase is what is wrong. (And I am not talking about whether it divides the load shorthand by L-G voltage or more mathematically accurately by RMS. ) This problem becomes more apparent as you add more load to the panel and especially if you had single phase two pole loads. I am not an engineer by training, but my engineers and designers tell me that the amps per phase is particularly important to consider in correctly sizing a panel. Granted, in my research thus far the amps per phase is always high rather than low, but it is still wrong.
From the screenshots, for example:
8333VA/120V=69A (Load per Phase/L-G Voltage)=Amps per Phase OR (Load per Phase*3/(208*sqrt(3))=Amps per Phase
If you select the panel, the properties display the current for phase A as 76A (screenshot Equipment). If you select the circuit (screenshot Circuit) from the panel to the switchboard, it displays the current for phase A as 69A. The load for phase A is the same for both. This is the root of the problem. The panelschedule only reports panel information, not circuit information, in this location on the panel schedule. If you look at Panel_208 you notice that I created rows for the correct calcuated values...for whatever reason that same formula in the phase columns of the schedule template produces incorrect values as well.
In case I am not communicating clearly...amps per phase as calculated for the panel and shown in the panel schedule is different(and wrong) than what it calculates for the amps per phase for the circuit (correct) from the panel to whatever feeds it.
I can also upload the test model if that would help. Thanks in advance for any help.